by Rich Kulawiec
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message It seems $dayjob needs one or two, somewhere in the 2u to 4u
range, for 2-4 low-end servers. Remote control is spiffy but not necessary; mostly I'm looking for something that gets the basics right before worrying about nice-to-have features. So... I figured I'd poll the collective wisdom. Thanks, ---Rsk _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Lionel Peterson-2
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sun, Oct 11, 2009 at 8:31 AM, Rich Kulawiec <rsk@...> wrote:
> It seems $dayjob needs one or two, somewhere in the 2u to 4u > range, for 2-4 low-end servers. Remote control is spiffy but > not necessary; mostly I'm looking for something that gets the > basics right before worrying about nice-to-have features. So... > I figured I'd poll the collective wisdom. At work we've had good luck with the various APC SmartUPS units, they have 2U (I guess) 2200 units that should keep a couple servers humming along through brief power outages (but may require 20 Amp circuits). New units are around $1K: http://www.newegg.com/Product/Product.aspx?Item=N82E16842101134&nm_mc=OTC-Fro ogle&cm_mmc=OTC-Froogle-_-UPS+(Back+Up+Power+Supply)-_-APC-_-42101134 But if you can stomach refurbs, here is but one example, older 3U SmartUPS 2200 with new batteries for $329: http://shop.1asecure.com/prod.cfm?ProdID=305425&StID=8432 Add-in management cards are available, and can be added later. The newer units have USB & serial, and honestly I think if you attach one server to the UPS, it can communicate to other machines on the UPS over the network (this is a function of PowerChute software, IIRC).... Lionel -- Lionel Peterson lionel4287@... _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Phil Stracchino-3
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Rich Kulawiec wrote:
> It seems $dayjob needs one or two, somewhere in the 2u to 4u > range, for 2-4 low-end servers. Remote control is spiffy but > not necessary; mostly I'm looking for something that gets the > basics right before worrying about nice-to-have features. So... > I figured I'd poll the collective wisdom. I still feel it's hard to go wrong with APC. -- Phil Stracchino, CDK#2 DoD#299792458 ICBM: 43.5607, -71.355 alaric@... alaric@... phil@... Renaissance Man, Unix ronin, Perl hacker, Free Stater It's not the years, it's the mileage. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Rich Kulawiec wrote:
> It seems $dayjob needs one or two, somewhere in the 2u to 4u > range, for 2-4 low-end servers. Remote control is spiffy but > not necessary; mostly I'm looking for something that gets the > basics right before worrying about nice-to-have features. So... > I figured I'd poll the collective wisdom. I think APC SmartUPS is the way to go. Also, I think this is a great item to buy refurbed, if money is tight. In particular, I like the guys at think3p.com, although refurbups.com has also been good. I bought my own 4U UPS (4U because it was cheaper than an equivalent smaller model) from think3p.com, which I originally found out about from this list. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Rich Kulawiec
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Thanks, everybody -- I'm going with your recommendation(s).
---Rsk _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Robert Darlington
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Consider Liebert. In my circle, APC sells junk. No matter what, if you
care about it, I'd go with AGM batteries in the very least. You'll wish you did when the day comes and you need to get the old gel cells out, but you can't because they swelled up and are permanently locked inside the equipment. -Bob On Mon, Oct 12, 2009 at 10:40 AM, Rich Kulawiec <rsk@...> wrote: > Thanks, everybody -- I'm going with your recommendation(s). > > ---Rsk > _______________________________________________ > rescue list - http://www.sunhelp.org/mailman/listinfo/rescue _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Phil Stracchino-3
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Robert Darlington wrote:
> Consider Liebert. In my circle, APC sells junk. No matter what, if you > care about it, I'd go with AGM batteries in the very least. You'll wish you > did when the day comes and you need to get the old gel cells out, but you > can't because they swelled up and are permanently locked inside the > equipment. I've only ever once had that happen on an APC UPS. APC sent us a brand new UPS with batteries and a prepaid shipping ticket to ship the old one back to them for failure analysis, because "That should never happen. We want to know what went wrong." -- Phil Stracchino, CDK#2 DoD#299792458 ICBM: 43.5607, -71.355 alaric@... alaric@... phil@... Renaissance Man, Unix ronin, Perl hacker, Free Stater It's not the years, it's the mileage. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Dan Sikorski
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Phil Stracchino wrote:
> Robert Darlington wrote: > >> Consider Liebert. In my circle, APC sells junk. No matter what, if you >> care about it, I'd go with AGM batteries in the very least. You'll wish you >> did when the day comes and you need to get the old gel cells out, but you >> can't because they swelled up and are permanently locked inside the >> equipment. >> > > I've only ever once had that happen on an APC UPS. APC sent us a brand > new UPS with batteries and a prepaid shipping ticket to ship the old one > back to them for failure analysis, because "That should never happen. > We want to know what went wrong." > > but I have had several APC's that have. I have noticed, however, that my Lieberts shut themselves down and refuse to power on when their batteries are at the end of their useful life, but the APC's keep going and light up the bad battery indicator. I haven't decided which behavior I like less. -Dan Sikorski _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Lionel Peterson-2
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Oct 12, 2009, at 12:56 PM, Robert Darlington
<rdarlington@...> wrote: > Consider Liebert. In my circle, APC sells junk. No matter what, if > you > care about it, I'd go with AGM batteries in the very least. You'll > wish you > did when the day comes and you need to get the old gel cells out, > but you > can't because they swelled up and are permanently locked inside the > equipment. I've seen that behavior in a Symmetra from APC, but our unit is old enough to have ZERO trade-in value. The battery trays swelled so much that we had to dis-Assemble the UPS to get them out, but I didn't consider that when making my recommendation because the OPs needs were an order of magnitude lower. APC rackmount-class UPSes have a great track record, in my experience. My only other experience was with wet cells in telco switching centers. I'd agree with Liebert for a datacenter-level need. Lionel _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Ethan O'Toole
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message I've had several APC UPSes that had battery swelling.
I've had small APCs that cut off when the batteries died. I've killed em by overloading them. You can get them cheap or for free with dead batteries then replace the batteries. -- .-[ Ethan O'Toole ]--------+ - - - - - - - - - +----. : FLICKR http://www.flickr.com/photos/ethanotoole : : HOMEPAGE " users.757.org/~ethan . `----------+ - - - - - - - - - +-----------=======--' _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by stephen price
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Wow - I just recently fought with 6 different units that I had to physically
disassemble to get the bloated cells out of every one of them. > Consider Liebert. In my circle, APC sells junk. No matter what, if you > care about it, I'd go with AGM batteries in the very least. You'll wish > you did when the day comes and you need to get the old gel cells out, > but you can't because they swelled up and are permanently locked inside > the equipment. > > I've only ever once had that happen on an APC UPS. APC sent us a brand > new UPS with batteries and a prepaid shipping ticket to ship the old one > back to them for failure analysis, because "That should never happen. > We want to know what went wrong." _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Patrick Finnegan
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Monday 12 October 2009, Robert Darlington wrote:
> Consider Liebert. In my circle, APC sells junk. No matter what, if > you care about it, I'd go with AGM batteries in the very least. > You'll wish you did when the day comes and you need to get the old > gel cells out, but you can't because they swelled up and are > permanently locked inside the equipment. The swollen battery problem seems to be caused by the UPS overcharging the batteries. The beige APC units seem to be bad about this, but I haven't seen it happen with the newer black units yet. I second Liebert, and add Powerware/Eaton. They both seem to have nice rackmount units. The only problem I have with the Liebert units that we had at work were that replacing the batteries wasn't trivial - you had to take the unit 1/2 apart to do it, which involves removing a couple dozen screws, and reaching around live battery parts (a 96VDC battery string) to disconnect the batteries. Other units probably aren't quite as bad. Pat -- Purdue University Research Computing --- http://www.rcac.purdue.edu/ The Computer Refuge --- http://computer-refuge.org _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Rich Kulawiec
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Mon, Oct 12, 2009 at 10:56:09AM -0600, Robert Darlington wrote:
> did when the day comes and you need to get the old gel cells out, but you > can't because they swelled up and are permanently locked inside the > equipment. I'm about to reveal the astonishing depths of my ignorance, but could you (or anyone) please explain why this happens? (I've done a bit of googling to try to spare you the question, but nothing I've gotten back seems to actually tell me what I'm trying to learn.) Thanks, ---Rsk _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Patrick Finnegan wrote:
> On Monday 12 October 2009, Robert Darlington wrote: >> Consider Liebert. In my circle, APC sells junk. No matter what, if >> you care about it, I'd go with AGM batteries in the very least. >> You'll wish you did when the day comes and you need to get the old >> gel cells out, but you can't because they swelled up and are >> permanently locked inside the equipment. > > The swollen battery problem seems to be caused by the UPS overcharging > the batteries. The beige APC units seem to be bad about this, but I > haven't seen it happen with the newer black units yet. > > I second Liebert, and add Powerware/Eaton. They both seem to have nice > rackmount units. The only problem I have with the Liebert units that we > had at work were that replacing the batteries wasn't trivial - you had > to take the unit 1/2 apart to do it, which involves removing a couple > dozen screws, and reaching around live battery parts (a 96VDC battery > string) to disconnect the batteries. Other units probably aren't quite > as bad. The Liebert that I removed batteries from was pretty simple. It was open door, turn a doohickey (not a thumb screw, but something with a tag to twist, no tool required), and pull the battery out. Nothing to fear in terms of personal damage, and no tools required. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Robert Darlington
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message The problem isn't so much that it's APC, it's that APC uses gel cells (aka,
SLA or sealed lead acid). These batteries swell, and sometimes even pop. AGM batteries do not do this. AGM batteries cost more, but it seems APC does sell some units with these batteries. I hate gel cells, but do use them occasionally where swelling isn't a concern, such as on my bicycle for the headlights. I would never consider them for something that mattered though. You won't see them in airplanes or submarines and you won't see them in my server room. A friend of mine worked with the state of Florida on some railway project. By random luck he noticed that there were service techs at railway crossings changing batteries for the lights that are used in case there is a power outage. He chatted them up about it and found out that they changed their SLA batteries out roughly once a month. Pat worked with them to come up with a solution. The first part was to add a heat shield (just a piece of aluminum over the box, spaced an inch or two over the box) and paint the box white (NOT silver). The other part was to replace the batteries with AGM batteries. Most of the batteries have now been in use for 26 years continuously. Gel cells can't take the heat, but AGMs don't like to be deep cycled. There are trade-offs, and I prefer to shut down servers before depleting the batteries (which results in just a delay before the cord gets yanked) This keeps the AGM batteries happy and it sure beats trying to pry out swollen batteries. On Mon, Oct 12, 2009 at 10:56 AM, Robert Darlington <rdarlington@...>wrote: > Consider Liebert. In my circle, APC sells junk. No matter what, if you > care about it, I'd go with AGM batteries in the very least. You'll wish you > did when the day comes and you need to get the old gel cells out, but you > can't because they swelled up and are permanently locked inside the > equipment. > > -Bob > > > On Mon, Oct 12, 2009 at 10:40 AM, Rich Kulawiec <rsk@...> wrote: > >> Thanks, everybody -- I'm going with your recommendation(s). >> >> ---Rsk >> _______________________________________________ >> rescue list - http://www.sunhelp.org/mailman/listinfo/rescue rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by Rich Kulawiec
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message It's amazing what you can learn hanging out on this list. Thanks, everybody.
---Rsk _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
UPS battery source? [was Re: Any recommendations on rack-mount UPS?]
by Scott Newell
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message All this talk of UPS and batteries reminds me that I need some new ones for
my Powerware 9125. I think it uses 4 x 12V 9AH. Anyone know of a good and inexpensive source in the US? thanks! -- newell N5TNL _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: UPS battery source? [was Re: Any recommendations on rack-mount UPS?]
by Dan Sikorski
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Scott Newell wrote:
> All this talk of UPS and batteries reminds me that I need some new ones for > my Powerware 9125. I think it uses 4 x 12V 9AH. Anyone know of a good and > inexpensive source in the US? > It may not work for you, but you might want to look into setting up a business account with Batteries Plus. Their normal retail prices for these batteries are high, but having a business account with them offers substantial discounts. We buy all of our standard sized replacement batteries from them. The werker ones that i buy for my APCs and Lieberts are a common size that they keep tons of in stock. After the recent conversations, I checked it out and found out that they are AGM SLA's. -Dan Sikorski _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: UPS battery source? [was Re: Any recommendations on rack-mount UPS?]
by Patrick Finnegan
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Wednesday 14 October 2009, Scott Newell wrote:
> All this talk of UPS and batteries reminds me that I need some new > ones for my Powerware 9125. I think it uses 4 x 12V 9AH. Anyone > know of a good and inexpensive source in the US? I usually get my batteries from Portable Power Systems. They have a good variety, both in battery type and quality/cost, depending on what you want to spend. Plus, they have an easy to remember URL: http://gotbatteries.com Pat -- Purdue University Research Computing --- http://www.rcac.purdue.edu/ The Computer Refuge --- http://computer-refuge.org _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: Any recommendations on rack-mount UPS?
by velociraptor
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Mon, Oct 12, 2009 at 1:19 PM, Robert Darlington
<rdarlington@...> wrote: > A friend of mine worked with the state of Florida on some railway project. > By random luck he noticed that there were service techs at railway crossings > changing batteries for the lights that are used in case there is a power > outage. He chatted them up about it and found out that they changed their > SLA batteries out roughly once a month. Pat worked with them to come up > with a solution. The first part was to add a heat shield (just a piece of > aluminum over the box, spaced an inch or two over the box) and paint the box > white (NOT silver). The other part was to replace the batteries with AGM > batteries. Most of the batteries have now been in use for 26 years > continuously. Gel cells can't take the heat, but AGMs don't like to be deep > cycled. There are trade-offs, and I prefer to shut down servers before > depleting the batteries (which results in just a delay before the cord gets > yanked) This keeps the AGM batteries happy and it sure beats trying to pry > out swollen batteries. AGMs handle all temp variation better, from what I understand. I only use AGM in my motorcycles now, especially in Vegas. Normal lead-acid cannot take the LV summer at all. =Nadine= _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
| Free embeddable forum powered by Nabble | Forum Help |